Is there anything prohibiting class 2 transformers from being paralled together?
Is there anything prohibiting class 2 transformers from being paralled together?
725.121 Power Sources for Class 2 and Class 3 Circuits.
(A) Power Source. The power source for a Class 2 or a
Class 3 circuit shall be as specified in 725.121(A)(1), (A)(2),
(A)(3), (A)(4), or (A)(5):
(1) A listed Class 2 or Class 3 transformer
More specifically would be 725.121(B)
(B) Interconnection of Power Sources. Class 2 or Class 3 power sources shall not have the output connections paralleled or otherwise interconnected unless listed for such interconnection.
More specifically would be 725.121(B)
(B) Interconnection of Power Sources. Class 2 or Class 3 power sources shall not have the output connections paralleled or otherwise interconnected unless listed for such interconnection.