210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel. Ground-fault circuit-interrupter protection for
personnel shall be provided as required in 2IO.S(A) through
(C). The ground-fault circuit-interrupter shall be installed in
a readily accessible 10catiol1.
Informational Note: See 2 \5.9 for ground-fault circuitinterrupter
protection for personnel on feeders.
(A) Dwelling Units. All J 25-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
21O.8(A)(I) through (10) shall have ground-fault circuitinterrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a
floor located at or below grade level not intended as
habitable rooms and limited to storage areas, work
areas, and areas of similar use
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a branch circuit dedicated to
electric snow-melting, deicing, or pipeline and vessel heating
equipment shall be permitted to be installed in accordance
with 426.28 or 427.22. as applicable.
(4) Crawl spaces - at or below grade level
(5) Unfinished basements - for purposes of this section,
unfinished basements are defined as portions or areas
of the basement not intended as habitable rooms and
limited to storage areas, work areas, and the like
Exception to (5): A receptacle supplying only a pennanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection.
lnformational Note: See 760.41(B) and 760.121 (B) for
power supply requirements for fire alarm systems.
Receptacles installed under the exception to
210.8(A)(5) shall not be considered as meeting the
requirements of 210.52(G)
(6) Kitchens - where the receptacles are installed to
serve the countertop surfaces
(7) Sinks - where receptacles are installed within 1.S m
(6 ft) of the outside edge of the sink
(8) Boathouses
(9) Bathtubs or shower stal1s -- where receptacles are
installed within 1.8 m (6 ft).of the outside.edge of the
bathtub or shower stall
(10) Laundry areas
(B) Other Than Dwelling Units. All 125-volt, singlephase,
15- and 20-ampere receptacles installed in the locations
specified in 210.S(B)( 1) through (S) shall have
ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2) Kitchens
(3) Rooftops
(4) Outdoors
Exception No. 1 to (3): Receptacles on rooftops shall not be
required to be readily accessible other than from the
rooftop.
Exception No. 2 to (3) and (4): Receptacles that are not
readily accessible and are supplied by a branch circuit
dedicated to electric snow-melting, deicing, or pipeline and
vessel heating equipment shall be permitted to be installed
in accordance with 426.28 or 427.22, as applicable.
Exception No, 3 to (4): In industrial establishments onl}~
where the conditions of maintenance and supervision ensure
that only qualified personnel are involved, an assured
equipment grounding conductor program as specfied in
590.6(B)(2) shall be permitted for only those receptacle
outlets used to supply equipment that would create a
greater hazard if power is interrupted or having a design
that is not compatible with G FCI protection.
(5) Sinks - where receptacles are installed within 1.S m
(6 ft) of the outside edge of the sink
Exception No. 1 to (5): In industrial laboratories, receptacles
used to supply equipment where removal of power
would introduce a greater hazard shall be permitted to be
installed without GFCI protection.
Exception No.2 to (5): For receptacles located in patient
bed locations of general care or critical care areas of
health care facilities other than those covered under
210.8(B)(l), GFCI protection shall not be required.
(6) Indoor wet locations
(7) Locker rooms with associated showering facilities
(8) Garages, service bays, and similar areas other than vehicle
exhibition hal1s and showrooms
(C) Boat Hoists. GFCI protection shall be provided for
outlets not exceeding 240 volts that supply boat hoists installed
in dwelling unit locations.
(D) Kitchen Dishwasher Branch Circuit. GFCI protection
shall be provided for outlets that supply dishwashers
installed in dwelling unit locations.