Class 1 division 1 im familiar with this is regarding a acetone recycler placed out side a paint booth area the equipment is class 1 div 1 and group D I am not familiar with group D requirements I do know im trying to keep my disconnect out of my class area for obvious reasons. SO what is the group D ?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
See Section 500.6(A)(4). You also should review NFPA 497 as referenced in the Informational Note to obtain the “T-Code” required in Sections 500.8(B) and (C)(4).
 