- Location
- Illinois
- Occupation
- retired electrician
In reading this EC&M article it appears that the only way to have a Division 2 location inside a building where flammable liquids or vapors are handled would be to have a ventilation or purge system. I know that is not the case for the facilities I work in that have interior Class I, Division 2 locations.
The following is from the EC&M article:
I think there is enough difference between 500.5(B)(1)(3) and 500.5(B)(2)(1) to permit interior Class I, Division 2 locations without a purging or ventilation system.
The following is from the EC&M article:
Div. 1 is the more stringent of the two divisions. In a Div. 1 location, the gas or vapor is (or may be) present under these conditions:
A Div. 2 exists in a Class I location only under the following three conditions [500.5(B)(2)]:
- During normal operation.
- Frequently due to repair, maintenance, or leakage.
- During equipment breakdown or faulty operation.
- The liquids, vapors, or gases are confined within closed containers or systems.
- Positive mechanical ventilation prevents “critical mass” accumulation.
- Positive mechanical ventilation prevents spillover from an adjacent Class I, Div. 1 location.
I think there is enough difference between 500.5(B)(1)(3) and 500.5(B)(2)(1) to permit interior Class I, Division 2 locations without a purging or ventilation system.
500.5(B)(1)(3) In which breakdown or faulty operation of equipment or processes might release ignitible concentrations of flammable gases, flammable liquid–produced vapors, or combustible liquid–produced vapors and might also cause simultaneous failure of electrical equipment in such a way as to directly cause the electrical equipment to become a source of ignition.
The article seems to ignore some of the wording in 500.5(B)(1)(1) and 500.5(B)(2)(3).500.5(B)(2)(1) In which volatile flammable gases, flammable liquid–produced vapors, or combustible liquid–produced vapors are handled, processed, or used, but in which the liquids, vapors, or gases will normally be confined within closed containers or closed systems from which they can escape only in case of accidental rupture or breakdown of such containers or systems or in case of abnormal operation of equipment, or