Class II Div 2

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Are there any practical differences between the wiring methods used for Class I Div 2 and Class II Div 2? What about receptacles and equipment? I have a nutraceutical operation trying to close out a fire alarm permit (not ours) and it looks like the room is, per the drawings, Class II Div 2. The fire alarm equipment is definitely not rated. I can put in some dual listed equipment, but was hoping to get guidance on some path closer to Class II.
 
Class II enclosures can realistically block the entrance of dust while Class I explosionproof don't even try. Dusttight is usually sufficient in Class II, Division 2.
 