N nhfire77 Senior Member Location NH Jan 19, 2018 #1 Anyone have a recommendation for a CO detector that is C3, div 2 rated..... that can Alarm at 30ppm? So far I’ve come across those that are 50 or 100ppm or higher (I realize it will probably be CII or CI rated anyway)
Anyone have a recommendation for a CO detector that is C3, div 2 rated..... that can Alarm at 30ppm? So far I’ve come across those that are 50 or 100ppm or higher (I realize it will probably be CII or CI rated anyway)
gadfly56 Senior Member Location New Jersey Occupation Professional Engineer, Fire & Life Safety Jan 19, 2018 #2 nhfire77 said: Anyone have a recommendation for a CO detector that is C3, div 2 rated..... that can Alarm at 30ppm? So far I’ve come across those that are 50 or 100ppm or higher (I realize it will probably be CII or CI rated anyway) Click to expand... Check this out. You'll need a specialty controller to go with it, but it will detect CO in the range of 0-500ppm at a resolution of 0.5ppm.
nhfire77 said: Anyone have a recommendation for a CO detector that is C3, div 2 rated..... that can Alarm at 30ppm? So far I’ve come across those that are 50 or 100ppm or higher (I realize it will probably be CII or CI rated anyway) Click to expand... Check this out. You'll need a specialty controller to go with it, but it will detect CO in the range of 0-500ppm at a resolution of 0.5ppm.