T tgreen Member May 2, 2012 #1 Has anyone seen a fues reducer, so that i can use a 400amp class L fuse in a 1200 amp class L fuse disconnect.
Has anyone seen a fues reducer, so that i can use a 400amp class L fuse in a 1200 amp class L fuse disconnect.
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems May 2, 2012 #2 There is no adapter. However, you can now buy Class fuses in sizes smaller than 601A (UL changed their listing requirements).
There is no adapter. However, you can now buy Class fuses in sizes smaller than 601A (UL changed their listing requirements).
G GearMan Member Location WI May 2, 2012 #3 jim dungar said: There is no adapter. However, you can now buy Class fuses in sizes smaller than 601A (UL changed their listing requirements). Click to expand... Really, Class L smaller than 601A? I have an application, what MFG should I look at?
jim dungar said: There is no adapter. However, you can now buy Class fuses in sizes smaller than 601A (UL changed their listing requirements). Click to expand... Really, Class L smaller than 601A? I have an application, what MFG should I look at?
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems May 2, 2012 #4 GearMan said: Really, Class L smaller than 601A? I have an application, what MFG should I look at? Click to expand... All of the manufacturers. Of course, distributor stock is another matter.
GearMan said: Really, Class L smaller than 601A? I have an application, what MFG should I look at? Click to expand... All of the manufacturers. Of course, distributor stock is another matter.