I have to rework an outdoor propane filling station. The existing circuit is fed underground in 3/4" RMC stubbing up by the tank with a sealoff 4' above the ground. After the seal there is a Cl 1 div 2 J-box. Above the box is a cl1 div 2 switch. The load side of the switch passes back through the j-box, into a pipe with a seal below the box to a cl 1 div 2 pump motor 10' away in the same area. Is this all that is needed as far as sealoffs? Does this meet all the requirements? From what I read it does. Can I use approved sealtite & fittings at the motor without additional sealoffs? Thanks,Scott