J jdero Member Location michigan Dec 13, 2010 #1 Art. 502.10 B (2) indicates that emt can be used in this area. My question is: do we need to use special fittings? dustight etc?
Art. 502.10 B (2) indicates that emt can be used in this area. My question is: do we need to use special fittings? dustight etc?
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Dec 13, 2010 #2 jdero said: Art. 502.10 B (2) indicates that emt can be used in this area. My question is: do we need to use special fittings? dustight etc? Click to expand... For the general raceway installation, Art 358 is suitable; however, pay close attention to Section 502.30 for grounding and bonding requirements. Also note that the requirements for Division 1 and 2 are the same for grounding and bonding.
jdero said: Art. 502.10 B (2) indicates that emt can be used in this area. My question is: do we need to use special fittings? dustight etc? Click to expand... For the general raceway installation, Art 358 is suitable; however, pay close attention to Section 502.30 for grounding and bonding requirements. Also note that the requirements for Division 1 and 2 are the same for grounding and bonding.