Having trouble finding something... I know a boundary seal is required for a conduit leaving a CL1 DIV2 location, but what about a near a man door that leaves the CL1 DIV2 location, going outside? I have been told that the area outside a man door (10' radius?) is also considered to be CL1 DIV2 within this radius, but I cannot find a section that specifies this.
It is a manufactured building, so I looked in Art 545, nothing there. It is not a garage or other specific occupancy with its own section, it is a pump room for disposal of fracking water. The reason it is CL1, DIV2 is because the water coming back out of the well can contain oil. it is generally separated out before disposal, but could possibly have oil in it, thus the CL1 DIV2 classification.
For the light fixture outside this man door, we were told this light has to be rated for CL1 DIV2 because of its proximity to the door, which is what I cannot locate in the code. The light is rated CL1 DIV2 in any case.
Additionally, if the space around the door is still considered to be part of the CL1 DIV2 space, then we really are not leaving the classified area with the conduit that feeds the light. Does that mean it could cross the wall boundary without a seal? Or is the space outside the door considered non-classified (if the radius around the man door information was incorrect)? If the area outdoors near the door is non-classified, I will definitely seal the boundary.
The safest thing is to probably just seal the boundary and end all doubt, but I was hoping someone could help me locate that bit about the space near the door, if it exists.
It is a manufactured building, so I looked in Art 545, nothing there. It is not a garage or other specific occupancy with its own section, it is a pump room for disposal of fracking water. The reason it is CL1, DIV2 is because the water coming back out of the well can contain oil. it is generally separated out before disposal, but could possibly have oil in it, thus the CL1 DIV2 classification.
For the light fixture outside this man door, we were told this light has to be rated for CL1 DIV2 because of its proximity to the door, which is what I cannot locate in the code. The light is rated CL1 DIV2 in any case.
Additionally, if the space around the door is still considered to be part of the CL1 DIV2 space, then we really are not leaving the classified area with the conduit that feeds the light. Does that mean it could cross the wall boundary without a seal? Or is the space outside the door considered non-classified (if the radius around the man door information was incorrect)? If the area outdoors near the door is non-classified, I will definitely seal the boundary.
The safest thing is to probably just seal the boundary and end all doubt, but I was hoping someone could help me locate that bit about the space near the door, if it exists.