That happens with the enforcement of every subjective rule in the code book. How can any subjective rule be enforced without "making up a rule"?
One of the best ones IMO is location of service disconnecting means - "nearest the point of entrance".
Many AHJ's actually have adopted their own official meanings to that as amendments or other rules, which I guess is better then each inspector in a jurisdiction having his own rule, but you run into places where you don't enter the building at all, some where it must be directly back side of point of entrance, some where they maybe allow certain length of service conductors anywhere from 3 feet to maybe 10 feet to be inside, some you can run service conductors just about any distance if vertical but have restrictions if any part of run is horizontal.