There is a disrepancy within our office interpreting the code on clearances, 110.26. The code requires that all disconnects be readily accessible 404.8(A). Working clearance is maintained at a clearance of 36" for voltages below 600V. There is an exception in 404.8(A)EX. 2, which states that if a disconnect is installed adjacent to the piece of equipment being supplied it can be mounted over 6'7" for qualified personel (such as a VAV or an AHU mounted above an acustical tile ceiling). In the handbook 110.26(a) page 45, states,"likely to require examination, adjusting, servicing, or maintenance while energized." Within the explanation block it says the intent that says,"Minimum working clearances are not required if the equipment is such that it is not likely to require examination, adjusting, servicing, and maintenance while energized."
What clarifies the statement, "not like to require." A typical situation, a VAV or AHU mounted above the ceiling. The disconnect can be mounted adjacent to it but does it need 36" for working clearance. The disconnect, theoretically, doesn't require any type of servicing or maintenance except maybe to test voltages, tighten a loose connection or change a fuse. But these procedures are not typical servicing such as adjusting internal components of a piece of equipment.
So, in conclusion, can a disconnect be mounted adjacent to a piece of equipment an not have 36" deep and 30" wide clearances, since the disconnect is not likely to require servicing?
What clarifies the statement, "not like to require." A typical situation, a VAV or AHU mounted above the ceiling. The disconnect can be mounted adjacent to it but does it need 36" for working clearance. The disconnect, theoretically, doesn't require any type of servicing or maintenance except maybe to test voltages, tighten a loose connection or change a fuse. But these procedures are not typical servicing such as adjusting internal components of a piece of equipment.
So, in conclusion, can a disconnect be mounted adjacent to a piece of equipment an not have 36" deep and 30" wide clearances, since the disconnect is not likely to require servicing?