Clearance of manufacturer live parts to enclosure

Status
Not open for further replies.
As always when I post here, I need an answer on the fly.

What is clearance of live parts, including our terminations to the enclosure and other metal parts? I appreciate the help.
 
As always when I post here, I need an answer on the fly.

What is clearance of live parts, including our terminations to the enclosure and other metal parts? I appreciate the help.
This should not be an issue for you because the equipment that you're terminating to should have this already incorporated into its design.
 
You can use Table 408.56 in the NEC as guidance, but the product standards, and not the NEC govern this issue.
 
Clearance to terminals for wires exiting an enclosure are also governed by "wire bending space", so without specifics on what you are referring to, there is no single answer.
 