- Lockport, IL
- Semi-Retired Electrical Engineer
Please see the attached photo. The red signal head was recently installed under a project I have since inherited. The comm line above it was existing. The first owner complaint was that the wires bump into each other. The contractor (part of the design/build team of which my company is the design arm) suggested installing a "fiberglass guy strain insulator" to keep the two cables separated. We are now being told by the owner that this does not meet clearance requirements. They cited 225.14 and 800.44(A)(4). Power to the signal head is well under 600 volts.
I cannot get this to make sense. For open conductors under 600 volts, 225.14 points to you the clearance requirements of table 230.51C. That table talks about spacing between supports, and then spacing between conductors. We do not have open conductors that are spaced certain distances apart. We have open conductors between two poles that are much farther apart than the distances in that table. So I don't think any part of this applies to my installation.
Next, 800.44(A)(4) speaks of clearances between a communication line entering a building and a power line entering a building, with both originating at the same pole. But we are not dealing with a service to a building, so I don't think that applies.
So what I need to know if whether there is a code section that established a minimum spacing between the two cables in the photo.