would like input on clearences for 13800 volt switch gear. i have a 13800 volt y system switchgear and a sheetrock wall opposite the switch gear. is it 4 ft. or 5 ft.
thanks vin
thanks vin
vincent antonellis said:yes i did , my problem is with the wording nominal voltage to ground does it change distance from 4 to 5 feet ?
dondon_resqcapt19 said:Vin,
Is the system a grounded system? I know that you said it is a wye system, but sometimes, where no single phase loads are served, XO is floated and you have an ungrounded wye system. If XO is floated, the voltage to ground is 13,800 volts and if XO is grounded the voltage to ground is 7980 volts.