sam asher
Member
- Location
- annapolis md
Any one know if there is a retro fit LED recess trim that is "identified for use in the closet storage area"
In our jurisdiction Halo RL series LED trims - RL560 and RL460 trims have been approved for use in a "closet storage space" - directly over a closet shelf - no clearance.
http://www.cooperindustries.com/con...sheets/halo-rl56-600series-td518021en-sss.pdf
See the attached spec sheet above under "compliance"
I'm not speaking of UL listing with other manufacturers housings - just Halo products.
In our jurisdiction Halo RL series LED trims - RL560 and RL460 trims have been approved for use in a "closet storage space" - directly over a closet shelf - no clearance.
http://www.cooperindustries.com/con...sheets/halo-rl56-600series-td518021en-sss.pdf
See the attached spec sheet above under "compliance"
I'm not speaking of UL listing with other manufacturers housings - just Halo products.
In our jurisdiction Halo RL series LED trims - RL560 and RL460 trims have been approved for use in a "closet storage space" - directly over a closet shelf - no clearance.
For the rest of us, those fixtures can NOT be placed inside the closet storage space. The "Compliance" section of that spec sheet cites "410.16 (C)(3)", which requires 6 inches between the fixture and closet storage area.
If it could go inside the storage area it would have instead claimed 410.16 (C)(5)
The only such light I've found is Legrande's 277FL. And the brochure doesn't speak to whether it satisfied C- 410 (C)(5), but I called Legrand, and was told that out does.
I also say that this trim is not suitable for use over the closet storage space. Look at the specific code sections- they state 6" etc....
It also states for use in closets but it does not state over storage areas
If retrofitting, the original can shouldn't have been in the storage area to begin with.Any one know if there is a retro fit LED recess trim that is "identified for use in the closet storage area"
Indeed! The webpage makes that claim, while the spec sheet speaks instead of 410.16(C)(3).The Halo RL56 series specifically state they comply with 410.16(C)(5) which allows fixtures identified for use in the storage space.