Obviously my info was outdated (as am I
) Thanks I'll remove the link from my computer
Augie, I would say not outdated. UL product Category IFDR does include special product markings, the category does cover lo voltage fixtures of all kinds but like all fixtures there a distinctive markings that shall be labeled & identified.
On a side note the defined area for insulation over non IC recess does make 2 separate comments.
2015 Whitebook Category IFDR
PRODUCT MARKINGS
Luminaires and fittings restricted for connection to a Class 2 source of
supply are identified by product markings.
These luminaires and fittings are intended for surface mounting, suspended
or recessed installation and are marked for either dry, damp or wet
locations. A luminaire or fitting marked for wet locations is rated no more
than 15 V ac or 30 V dc unless live parts are made inaccessible to contact
during normal use. See Luminaires and Fittings (HYXT) for additional
installation markings.
Low-voltage luminaires that have been investigated for use within the
storage area of a clothes closet are so identified on their installation instructions.
Recessed units (luminaires and power units) marked ‘‘Type IC’’ or
‘‘Inherently Protected’’ may be installed in accordance with Section 410.66
of the NEC, such that insulation and other combustible materials are in
contact with and over the top of the unit.
All recessed units not marked ‘‘Type IC’’ or ‘‘Inherently Protected’’ are
intended to be installed such that insulation is
not placed over the top or
within 3 inches of the sides of the unit, and other combustible materials
are spaced, except at the points of support, at least 1/2 inch from the unit.
Power units shipped separately from the bare conductor lighting system
are marked to identify the associated bare conductor system series number
and manufacturer.