hello,
per NEC 410.16 you can install an incandensent luminaire in a clothes closet if the light source is completely enclosed.
Are we still required to comply with the spacing requirements of NEC 410.2?
I have an existing condition where there are enclosed incandescent lights installed in a clothes closet. The owner is asking if this is code compliant. I have not been to the site to verify if it meets the spacing requirements. If it does not need to comply with 410.2, then it appears that we are OK with leaving them in place, even if they do not meet the spacing requirements. If we are still required to comply with 410.2, then I will make the site visit.
Thanks
per NEC 410.16 you can install an incandensent luminaire in a clothes closet if the light source is completely enclosed.
Are we still required to comply with the spacing requirements of NEC 410.2?
I have an existing condition where there are enclosed incandescent lights installed in a clothes closet. The owner is asking if this is code compliant. I have not been to the site to verify if it meets the spacing requirements. If it does not need to comply with 410.2, then it appears that we are OK with leaving them in place, even if they do not meet the spacing requirements. If we are still required to comply with 410.2, then I will make the site visit.