Club wired with romex?

Status
Not open for further replies.

Chong

Member
Cant get through to the city inspector so I will ask here. The building is 1500 sq. ft., wood frame, and will hold 127 people. Do I have to use MC cable and EMT or can I use romex? Thanks.
 
Re: Club wired with romex?

is this building a place of assembly, if it is,
look at 518.4, need more info if not.
 
Re: Club wired with romex?

1500 divided byt 127 = a little over 11 sq feet per person not allowing for bathrooms.Dang thats packing them in .What kind of club is this ?Being its 100 people i think your forced not only into mc or pipe but a lot of other things like emg lights ,fire exit signs
 
Re: Club wired with romex?

11 sq ft./ person that is what i would call 2nd class seating ;) as stated if a place of assembly then other wiring methods would be required :cool:
 
Re: Club wired with romex?

If it is wood framed, obviously it is not type I or II construction, so 334.10(A) would not be an issue. Aside from that, the places of assembly rules would prevail. I highly doubt that it is one hour construction, however.
 
Re: Club wired with romex?

It will be a dance club. It is in a poor part of town and looks like a house that doesn't have any walls inside, its just 1 big room. The owner said the city inspector came by and told him about all of the permits he will need to have pulled. I don't have a code book in front of me so I'm guessing this is considered a place of assembly and romex wont be exceptable. Just because its a wood frame building doesn't automatically mean I can use romex?
 
Re: Club wired with romex?

I thought most clubs consisted of 3 pieces of bread, turkey, bacon, lettuce, tomato and mayo?

Where does the romex come into play? :confused:

[ March 29, 2005, 10:17 PM: Message edited by: peter d ]
 
Re: Club wired with romex?

Originally posted by peter d:
I thought most clubs consisted of 3 pieces of bread, turkey, bacon, lettuce, tomato and mayo?

Where does the romex come into play? :confused:
Having come to this website for 5 years now I allways thought of it as a place to go for professional advice. Unfortunately this is the type of reply that most people can expect to receive when they ask a question. Sorry if I cant find the humor in the above reply.
 
Re: Club wired with romex?

dude you gotta learn 2 chill after long hard days IN THE FIELD we have to be able to joke with each other in this forum. as far as wood equals romex the answear is no we just wired a small era building in mc cable depends on specs in a club I would definitely go with mc and emt ummmmmm club sandwich
 
Re: Club wired with romex?

Chong, :roll:

[ March 29, 2005, 11:27 PM: Message edited by: physis ]
 
Re: Club wired with romex?

I edited both of these because I think it's better I don't say anything.

[ March 29, 2005, 11:28 PM: Message edited by: physis ]
 
Re: Club wired with romex?

i think i answered in a very professional manner.More info is needed as far as the oyhers ,well thay are suffering from switched dining room outlet syndrom :D That takes awhile to get over after long sessions on the couch :D
 
Re: Club wired with romex?

I have been scared to even go into my dining room because my wife has her computer in there and has a lamp pluged into an outlet.Should i call the local AHJ and have her arrested ? Will i get fined over this violation ? :confused: :confused:
 
Re: Club wired with romex?

places of assembly do not automatically rule out NM cable. 518.4(B) allows NM in buildings not required to be of fire-rated construction. As Ryan pointed out, this building in question is not likely to be required to be of rated construction.
 