e57

Senior Member
More Inspector follies - Inspector say coated J-nails not approved for support of NM feeder cable - that they are only approved for use on conduit. What say you? Why? Why not?
 
I use drive straps from time to time to hang large cables. They work great for that. As far as I'm concerned, I don't care if you tie it up with little ribbon bows. If it works, it works. The mere existence of hangers and straps specially designed for this application does not, in and of itself, necessitate their use by any means.
 
In this same conversation - would you think a 9/16 staple with the same sized 1/0 copper SEC/NM* cable ZIP-TIED to it be an approved use????

And yes - what about a strap of NM sheath tied in a bow?

String? Rope?

Do straps and supports need to be listed????? Approved even????

similar fittings designed and installed so as not to damage the cable

*Both list the same support means.
 
e57 said:
In this same conversation - would you think a 9/16 staple with the same sized 1/0 copper SEC/NM* cable ZIP-TIED to it be an approved use????

And yes - what about a strap of NM sheath tied in a bow?

String? Rope?

Do straps and supports need to be listed????? Approved even????



*Both list the same support means.

Yes to the 9/16th staple and zip tie, as long as it is a reasonable size zip tie.
Is this the same inspector (lets call him Mr. Not Nice) that dinged you on the basin receptacle ?
 
mdshunk said:
I use drive straps from time to time to hang large cables. They work great for that. As far as I'm concerned, I don't care if you tie it up with little ribbon bows. If it works, it works. The mere existence of hangers and straps specially designed for this application does not, in and of itself, necessitate their use by any means.

Straps must be listed for use as a strap for a specific purpose.
I'll find a code reference for you later.
I have heard of inspectors calling guys on using improper sized nm straps for 3 or 4 cables before.
 
alfiesauce said:
Straps must be listed for use as a strap for a specific purpose.
I'll find a code reference for you later.

Good luck with that. :smile:

Beyond 110.3(B) I don't believe you will find any.
 
theres a lot of service cable that was supported with J nails, that has been on peoples houses for many, many years with no problems, I didn't know anybody still used J nails.
 
alfiesauce said:
Straps must be listed for use as a strap for a specific purpose.
I'll find a code reference for you later.
Yeah, best of luck with that. While you're at it, find me some listed screws to hold up my jiffy clips.
 
acrwc10 said:
Yes to the 9/16th staple and zip tie, as long as it is a reasonable size zip tie.
Is this the same inspector (lets call him Mr. Not Nice) that dinged you on the basin receptacle ?
Lets say yes....
 
alfiesauce said:
Straps must be listed for use as a strap for a specific purpose.
I'll find a code reference for you later.
I have heard of inspectors calling guys on using improper sized nm straps for 3 or 4 cables before.
iwire said:
Good luck with that. :smile:

Beyond 110.3(B) I don't believe you will find any.
mdshunk said:
Yeah, best of luck with that. While you're at it, find me some listed screws to hold up my jiffy clips.
nec2008SEWhatif.png

Ya never know :D
 