code 230.3

Status
Not open for further replies.

ckgeneral

New member
Hello everyone, sorry for the abrupt question asking....I have a property w/ two units on it that I am working on (Front unit is two condos, back unit is one - they are about 20 feet apart). I need to run a 200amp from the front unit to back, but cannot do it underground. Is it possible to run it through the basement up the main house then across to the back unit? Also does anyone have the NEC code 230.3 that they could post?

Thank you in advance for your help.
 
Re: code 230.3

230.3 One Building or Other Structure Not to Be Supplied Through Another. Service conductors supplying a building or other structure shall not pass through the interior of another building or other structure.

Since the units appear to be rentals, this should be done by a licensed electrical contractor.

Roger
 