Why would this matter? It is not currently compliant.If the "3-wire sub panel" is located in an outbuilding, so that the existing ungrounded feeder is allowed for continued use, then the EGC system gets reestablished at the sub panel with a N-G bond, and it would be fine to run a 4-wire feeder from there, right?
Cheers, Wayne
We don't actually know that. If the subpanel referred to in the OP is in an outbuilding, then being supplied by an ungrounded feeder would be compliant for an existing install.Why would this matter? It is not currently compliant.
It was (maybe) compliant when installed. It was legal until the 08 code I believe. May have been a cycle either way, but somewhere in that time frame it was compliant. If the neutral & EGC are bonded in the subpanel, and a GEC and electrode is installed, I don't see a problem with running a 4-wire from there to a new subpanel. Of course the new subpanel would have to comply with current code with neutral & ground separated.Why would this matter? It is not currently compliant.
I don't know how much you are allowed to add to an existing piece of hardware that is no longer compliant.It was (maybe) compliant when installed. It was legal until the 08 code I believe. May have been a cycle either way, but somewhere in that time frame it was compliant. If the neutral & EGC are bonded in the subpanel, and a GEC and electrode is installed, I don't see a problem with running a 4-wire from there to a new subpanel. Of course the new subpanel would have to comply with current code with neutral & ground separated.
Grandfathered means it is NOT compliant but allowed to remain in service.I tend to agree. "Grandfathered" implies compliant. It's functionally an extension of the service. As long as it includes proper electrode(s), I see no reason a compliant feeder can not be supplied from it.
Right. By "compliant" I mean compliant when installed under past rules, and allowed to remain in the present rules.Grandfathered means it is NOT compliant but allowed to remain in service.
What code would prohibit supplying a 4-wire feeder from a legal-when-installed 3-wire-fed sub-panel?It is compliant for the existing panel in the other building, we don't know if that is the case here, but adding another panel, IMO is not compliant
I've pulled feeders off of several fused panels. Usually I use one of the pull-out fuse blocks to feed the subpanel. Then take the load that was on the fuse block and add it to the subpanel. No problem in sending 4 wires from that to the sub.I don't know how much you are allowed to add to an existing piece of hardware that is no longer compliant.
The Op seemed to indicate maybe it was a fused panel. I am not sure there is a compliant way to tack on to an existing fuse style panel.
he may also find he has a load problem once he does his load calculations.
What code would prohibit supplying a 4-wire feeder from a legal-when-installed 3-wire-fed sub-panel?
The 3-wire sub-panel, with a neutral/ground bond, looks exactly like a service panel to the new feeder.
The hypothetical that I posited, that the subpanel is in a detached building (which is what grandfathered 3 wire subpanel brings to my mind) is allowed under 250.32(B)(1) Exception 1, and hence is compliant with both of the sections you referenced.250.24(A)(5), 250.142(B).
The hypothetical that I posited, that the subpanel is in a detached building (which is what grandfathered 3 wire subpanel brings to my mind) is allowed under 250.32(B)(1) Exception 1, and hence is compliant with both of the sections you referenced.
Cheers, Wayne