code exam question
PCBERRY
Exam question; A 20 amp 240 volt single phase copper branch circuit supplying lighting on a metal pole at a traffic intersection shall be permitted to contain; a)2#8 &#8gr b) 2#10 &#12 gr c) 2#10 when polebase is bonded to the rebar cage d) 2#12 when a ground rod is driven
2#8 and #8 ground since all other options appear to be non code compliant
You got it
I agree too, your code reference would be 250.122(B)
Roger
Roger
Thanks for code there Roger.
I remembered this question as someone asked it recently....I wanted to link to it for the OP ~ but cannot find it.
Do you recall that thread?
I have a great memory...I just can't remember where I read stuff.....or where my car keys are at :D
Uh-oh. Prepare for a barrage of "Where does the NEC permit the EGC to be smaller than the BC conductors when using #10 or smaller?"
OK ready for the barrage.:D
250.122(B) requires that when ungrounded conductor are increased in size the equipment grounidng conductor must increased in size proportionately according to the circular mil area of the ungrounded conductors.
Chris