ryan_618 said:It was a change in the 2002 code. It was basically a trade off between the pipe gods and the romex gods for the three story limitation that was removed.
Volta said:Can't be used exposed above commercial dropped ceilings (334.12A2), commercial garages w/ hazardous locations (334.12A4), in buildings of type I or II construction (334.10(3)), others listed in 334.12.
Not otherwise generally prohibited.
realolman said:Where are these building types described?
thanks