code location on romex not used in commercial location

Status
Not open for further replies.

Eddie Joe

New member
We are trying to find a code location as to where we can't use romex in commercial locations. the building is one story and 1k sq ft. It has existing romex in the ceiling.
 
Article 334. There is no prohibition against using romex in a commercial building. The restrictions are based on building construction type.
 
NM

NM

Can't be used exposed above commercial dropped ceilings (334.12A2), commercial garages w/ hazardous locations (334.12A4), in buildings of type I or II construction (334.10(3)), others listed in 334.12.
Not otherwise generally prohibited.
 
I was just discussing this today at work. A coworker asked when the rule was put into the code prohibiting NM from being installed above drop ceilings. I did not know the answer. Does anyone know the history and or the substantiation for this change. My handbook says it was a 2005 change.

Joe
 
ryan_618 said:
It was a change in the 2002 code. It was basically a trade off between the pipe gods and the romex gods for the three story limitation that was removed.

And there is no safety reason that it could not be installed above a dropped ceiling.
 
Not allowed where I am.... It might be where you are. But it would be kind of embarassing to find out during an inspection....

I once saw a restuant TI/build out progress in NM as I walked by a window everyday for lunch. It was being done by an out of town EC, I left a very friendly note on his windshield - and the job progressed.... :rolleyes: A few days later there was a big pile of a few thousnad feet of NM on the floor and a new EC. I think it is safe to assume the original EC lost his shirt.
 
Volta said:
Can't be used exposed above commercial dropped ceilings (334.12A2), commercial garages w/ hazardous locations (334.12A4), in buildings of type I or II construction (334.10(3)), others listed in 334.12.
Not otherwise generally prohibited.

Where are these building types described?

thanks
 
realolman said:
Where are these building types described?

thanks

There better described in the building code. For example, a typical stadium would be concrete and steel, but it can be type V construction. I'm not saying you would (or even physically could) build it with wood, but it would be allowed as type V.

The best thing you can do is look at your approved (city stamped) set of plans and look at the code details. There should be things such as sqaure feet, occupancy classification(s) and type of construction listed.
 