B bizzy1978 New member Mar 17, 2008 #1 I was asked to put a disconnect 5 ft 6 in A.F.F to bottom. Is there a code stating a max height for the disconnect? Location control rm for a X ray machine.
I was asked to put a disconnect 5 ft 6 in A.F.F to bottom. Is there a code stating a max height for the disconnect? Location control rm for a X ray machine.
roger Moderator Staff member Location Fl Occupation Retired Electrician Mar 18, 2008 #2 See 404.8(A) Roger
radiopet Senior Member Location Spotsylvania, VA Mar 18, 2008 #3 Also if the Disconnect is also the OCPD ( which may not be the case but good to know ) then look at 240.24 as well ( change for 2005 NEC ) But if only a "Disconnection Means" then 404.8(A) would apply.
Also if the Disconnect is also the OCPD ( which may not be the case but good to know ) then look at 240.24 as well ( change for 2005 NEC ) But if only a "Disconnection Means" then 404.8(A) would apply.