Re: Code related Theory question
Ed, I contend that the precision of our numbers is only good to 3 significant figures, therefore we cannot reliably compute the resistance of 20K and 0.0135 Ohms in parallel. True the parallel resistance will be reduced a smidgen, but that is inconsequential in this problem.
Using Ed's numbers, the problem boils down to:
I = 2.7V/20K = 135 microAmps
If we assume R to be 150K, then:
I = 18 microAmps
If the man feels a tingle, it would be from the 2.7V, not from the 480.
Now if he is barefoot on a damp concrete floor, the current is:
I =480/20K = 24mA
But, that is line to line voltage; line to ground voltage should be less, but the poor guy would still be in a heap. I have read that currents in the order of a few milliAmps cause the body to throw itself away from the contact and possibly save the man's life.