I thought I understand it good that this for combustible material only, I thought if your walls are metal studs and sheetrock your box can be set up back more than 1/4 inch.
Is anybody have different opinion.
Is this ring will fix it
Thank you for our help.
View attachment 15133
If you use that metal ring then, IMO, you must ground it to the box
That's why I use the plastic ones by Arlington.
That's why I use the plastic ones by Arlington.
:thumbsup:
The "adjustable" boxes have not become popular here and Mr. Arlington should have been able to purchase a new car based on sales in this area due to the popularity of walls/ceilings finished with 3/4 thick lumber.
![]()
![]()
My inspectors have always required it. Used those ground clip dohickies. I suppose one could say that the metal to metal contact of a device to the extension ring satisfied bonding requirements, but it was easier to comply.
I respectfully disagree
First They are grounded via the screw and the contact with the yoke of the receptacle or the switch.
Second, that method of grounding was allowed until the early 90's even for receptacles.
Third, the metal isn't even exposed, as it is covered by a plate.
Fourth, if you need to run a supplemental ground those then by extension wouldn't you need to also run a supplemental ground to a stainless steel cover plate.
One is a loose connection the other is not.
Note that, with plastic boxes anyway, the cost of those extension rings and original box exceeds the cost of an adjustable box, especially when you consider the extra labor of futzing around with stackers and extra long 6-32 screws to mount your devices.
As others have written, boxes must be flush if the surrounding surface is combustible, like wooden paneling, and may be up to 1/4" inset/recessed from non-combustible wall surfaces like drywall. If you are more than 1/4" recessed, you neeed an extension ring/box extender like you linked.
Zip boxes are quite a bit more than cheapie plastic boxes, tho not a whole lot more than your sturdier, higher ci boxes. Some areas, like kitchen countertop boxes and receptacles in baseboard trim, it works out better in many cases to put in the zip box. What happens when the HO decides to add (or delete) a tile backsplash, or orders bb trim a different thickness than what you planned for? With a zip box, that inset or poking out box is fixed in 3 seconds for no additional cost on your end.
eta: stud type has no bearing on 314.20; it is only the wall finish that matters.