Carultch
Senior Member
- Location
- Massachusetts
Hello All,
I have an existing 150kVA delta - delta 480V-240/208/120V. The secondary is center grounded between phase A and C (Van=Vcn=120V). Phase B is usually called 'high leg' (Vbn=208V).
The EVCS (Electric Vehicle Charging Station) is Leviton ever-green Level 2 charger using SAE J1772 standard with this Elec input info:
- Input power: 7.2kW.
- Input voltage: 208/240VAC.
- Input current: 30A.
- Input power connections: Line 1, Line 2, Earth. (I see Neutral mentioned in their cutsheet for Level 1 but not for this Level 2 which is the product will be used in this case)
- Recommended breaker: 40A double pole breaker on a dedicated circuit.
What I'm getting at is, from the 150kVA transformer secondary via a 400A 3 phase, 4 wire panel, I can use 40A two pole breaker between phases AB, BC and CA (240V) to feed the EVCS. And I don't have to worry anything about the fact that it's a delta transformer with 'high leg' phase B.
I need to contact the manufacturer to see how efficient charging station is but for now let's assume 1kVA = 1kW.
This is the maximum charging stations I can hook up to the 150kVA transformer: 150/7.2 = 20.8333 so the max is 20 stations.
Please let me know if my calculation is wrong. Thanks.
There is a difference between SLASH RATED and STRAIGHT RATED breakers. Most single pole breakers are slash rated, meaning they are rated for 120/240V.
A breaker connected to the neutral and the high leg will experience 208Volts. If it is slash rated, it is not rated to exceed 120 Volts to ground. Even if it is rated for 240V to the neighboring phase.
It is rare that the high leg is usable. If it is, you would need a straight rated breaker. Rated at 240 volts no matter what.
All 3-pole breakers are straight rated, but not all 2-pole or 1-pole breakers are. Straight rated 2-pole breakers would be a lot more common than straight rated 1-pole.