e57
Senior Member
- Location
- San Francisco, CA
You would not have to derate the wiring in the gutter/wireway because all would be under the 30 limit - but the conductors in each conduit would be de-rated, because they each have 'more than three CCC's'... As required by 310.15(B)(2) It is one of the funnier math items in the code when it comes to the 310.16-19 tables. It also creates the misnomer of the "9 conductor rule" In most cases ambient temp is not enough to bring a circuit below commonly used circuit ratings because the values listed in 310.16 are higher, when derated at the very moderate amounts of 70% it often has no dramatic effect. (As listed in Table 310.15(B)(2)(a) up to 9 conductors are derated at 70%)benaround said:You have a wireway with 10 conduits entering the top, each have 9 CCC.
In the back of the wireway you have 10 conduits that line up with the top.
So you have 90 CCC total, but the wires run from top conduit to back conduit
directly below it. Do you need to derate at all ? I say 'no' because nothing
crosses.
Ya know this thread is just screaming for a bunch of graphic and pictures...