spotted123
Member
- Location
- South Texas
Is this transformer subject to NEC or is it POCO transformer?
Is the secondary 480 volt delta? If so is it an ungrounded system? If it were a 480/277 I would expect to see a terminal labeled X0 instead of just an unmarked lug on the tank. If it is corner grounded then depending if this is utility controlled or NEC application we may see the bond in the transformer housing, but either way one of the phases should be using white or gray as color of the grounded conductor.
What is with the white mark on one of the brown leads and one of the orange leads?
I suspected it was ungrounded. Biggest thing I can see is the two conductors in one lug that I'm fairly certain is not designed for two conductors.These are not POCO owned. The secondary is a 480 volt delta ungrounded system supplying an outdoor switchboard. I have no idea what the white tape on the brown & orange wire means.
I was thinking about that some but did not comment, no real experience with medium voltages.Oh....I just looked at a picture of bonding for a SDS. Seems weird to have a ground wire in with primary medium voltage cable, but if I'm looking at it right, I guess it's required. I'll stick to services.
I don't see anything exciting on the HV side. The grounds connected to the HV cables are just the shields. No neutral to be seen. The HV Red/White/Blue is standard POCO phase marking. [Go look at a phase rotation meter]
I was thinking about that some but did not comment, no real experience with medium voltages.
But I think the concentric neutral is also bonded to this additional EGC, can't quite tell for certain. If so there really isn't any purpose of running the separate EGC - it has become parallel to the concentric neutral. Another thing to consider is whether or not the transformer has Wye primary that actually needs a neutral connected to it or if it only needs the three phase conductors. If it needs a neutral then in NEC applications you need a neutral that is isolated from the EGC. In that case I would think (again not having any real experience with medium voltage) that it may be wiser to run an additional neutral conductor (may even need to be MV conductor) and use the concentric conductor(s) as the EGC.
If you're not familiar with underground primary cable, here's a bit of info....the "shield" as you call it, is the neutral on a grounded Wye primary. That's why a single phase transformer only has one cable going to it. Called a concentric neutral. The cable is built like a giant coax cable, but it has two conductors. The center conductor is the phase and the outer "shield" is the neutral. Separated by insulation and semi-conducting sheathing that reduces losses. Some Wye Delta transformers have a separate H0 neutral bushing that is insulated and externally bonded to the enclosure, and others are internally bonded. I like externally bonded, because you can lift the bond and megger the transformer windings while they're not grounded. Also, primary phase marking is not necessarily RWB on the primary. White is usually reserved for neutral to eliminate confusion. We use Red/Yellow/Blue. You don't use rotation meters on medium voltage cables. Why they colored them RWB is anyone's guess. Probably because it's easy to remember (if you're an American). Not trying to be picky...just that some folks might not know. Gotta go try to get some sleep...forest fire smoke is killing me!
The white wire for the potential tap appears to be part of a flexible cord. The use of white color would be permitted but needs to be reidentified, but the use of flexible cord is probably not permitted here, unless there is something we can't see that would justify it's use, seems pretty unlikely though.Since you are not a POCO, I don't believe you can use the white potential tap wire on the yellow LV leg as a hot wire. Even if you are using it for a metering/relaying source. If you wrapped a piece of yellow tape around it on each end, it might be ok. Is the voltage rating of the cable / cord high enough for an UNGROUNDED 480 delta? Probably if it is 600V. Not if it is 300V.
I don't see anything exciting on the HV side. The grounds connected to the HV cables are just the shields. No neutral to be seen. The HV Red/White/Blue is standard POCO phase marking. [Go look at a phase rotation meter]
Marking primary phases will correspond to specific secondary phases which they will connect to a rotation meter that most likely has RWB leads.If you're not familiar with underground primary cable, here's a bit of info....the "shield" as you call it, is the neutral on a grounded Wye primary. That's why a single phase transformer only has one cable going to it. Called a concentric neutral. The cable is built like a giant coax cable, but it has two conductors. The center conductor is the phase and the outer "shield" is the neutral. Separated by insulation and semi-conducting sheathing that reduces losses. Some Wye Delta transformers have a separate H0 neutral bushing that is insulated and externally bonded to the enclosure, and others are internally bonded. I like externally bonded, because you can lift the bond and megger the transformer windings while they're not grounded. Also, primary phase marking is not necessarily RWB on the primary. White is usually reserved for neutral to eliminate confusion. We use Red/Yellow/Blue. You don't use rotation meters on medium voltage cables. Why they colored them RWB is anyone's guess. Probably because it's easy to remember (if you're an American). Not trying to be picky...just that some folks might not know. Gotta go try to get some sleep...forest fire smoke is killing me!
If the install is covered by NEC and the primary utilizes the neutral, we must have separate grounded and grounding conductors, there should be a service disconnecting means somewhere upstream, and the primary neutral can not be bonded to the enclosure, the short version of what I was trying to point out earlier. This all started with the questioning of the green wire pulled with the primary cables.After looking at it again, maybe it IS a Delta primary. The wire bonding the concentric to the ground is pretty small for it to be a neutral. Nice if we could see the nameplate. Oh well....if it is, forget everything I said (if you haven't already).
[Marking primary phases will correspond to specific secondary phases which they will connect to a rotation meter that most likely has RWB leads.]
In my world, we always mark primary with the same colors regardless of voltage and set rotation CW ABC at loads. I don't tkink there's an industry standard color code. I have never seen Wh used as a phase, though. If it's an existing service that requires reverse rotation, we put a big sticker saying so on the meter panel. In the field, primary phasing can be a real headache if a standard is not used everywhere because switching of primary between subs must phase when being paralleled. We just went through our entire system identifying phases from each substation to every switch where paralleling can happen and put new colored phasing tape on every connection. Took months. Rotation is only half of the issue. A must be A, etc. Otherwise, the protective relaying can give bogus information on which phase is faulted. That can send the line crews on a wild goose chase. There are a few spots where phasing is incorrect and can't be rewired due to customer loads, so we put BIG "Does Not Phase" signs on the poles or padmount switches to help prevent smoke and flames.
[If the install is covered by NEC and the primary utilizes the neutral, we must have separate grounded and grounding conductors, there should be a service disconnecting means somewhere upstream, and the primary neutral can not be bonded to the enclosure, the short version of what I was trying to point out earlier. This all started with the questioning of the green wire pulled with the primary cables.
230.200 General.
Service conductors and equipment used on circuits exceeding 1000 volts, nominal, shall comply with all the applicable provisions of the preceding sections of this article and with the following sections that supplement or modify the preceding sections. In no case shall the provisions of Part VIII apply to equipment on the supply side of the service point.
Pad mounted transformers- 12.4kv primary-480vac secondary. Co-worker believes grounding and bonding is in violation. While I agree its sloppy work but not a violation. What do you think?
These are not POCO owned. The secondary is a 480 volt delta ungrounded system supplying an outdoor switchboard. I have no idea what the white tape on the brown & orange wire means.