Ok, this is delta. Sorry about the scattered reply, just opened the thread haven't read it all.
Its not a violation, however on most delta services bond wires aren't run from the switchgear to the transformer... at least this is how utilities do it. Most utility owned delta secondary PAD and pole pig banks only have 3 wires coming from the customer and nothing else. In fact some POCOs even discourage it, I will give an example.
However, as far as I know tying the secondary EGC to the HV EGC is not a violation. Whether its desirable or not is based on engineering requirements.
If it is not POCO equipment and NEC applies - it is not service equipment - it is a separately derived system just like a 480 to 208/120 transformer is. Should the primary circuit of that transformer require a neutral conductor for proper operation then NEC would require a separate neutral and separate EGC on the supply side, all the way back to wherever the service is or to the next upstream separately derived system originates if still NEC application at that point.
Any particular POCO standards or practices are meaningless if it is an NEC application.