I had planned a PV racking system using empty RMC as part of the support structure. Then I stumbled on the following from the Steel Tube Institute, which caused me to revisit it, and plan for fence pipe instead.
While researching it further, I seldom found any alloy identifier or strength rating on any RMC datasheet. The stiffness young's modulus for deflection calculations is the same for nearly all alloys of ferrous steel, but the strengths are different. I did end up finding one RMC datasheet that had a yield strength of around 26 ksi (can't remember where). Compare this with plumbing and structural pipe where the weakest pipe available is 30 ksi. It is plausible that RMC is intentionally weaker steel, so that it can be bent in the field. Possibly steel that is weak in yield strength and strong in ultimate strength, which would be desired for steel that is intended for reshaping at room temperature.
https://steeltubeinstitute.org/steel-conduit/frequently-asked-questions/
Question: Is RMC the same as Schedule 40 pipe?
Answer: No. The term “Schedule 40” originated with an ASTM specification and has come into general usage. It is still addressed in a number of ASTM specifications, whose requirements typically include dimensional and strength parameters.
Rigid conduit is intended for electrical applications, not structural ones. Its requirements are governed by UL and ANSI specifications, not by ASTM. The main issue here is that, whereas dimensions may be similar between the two, rigid conduit is not intended for, is not designed for, and is not tested for any strength or structural requirements
If a job specification calls for “schedule 40 conduit” or “schedule 40 rigid” confirm that the requirement is for rigid steel conduit, since “schedule 40” is still a term that applies to PVC conduit.