jim dungar said:Bob,
Your answers seem to be based on "I don't like it".
Your right I don't like it.
I have also provided code references to back that dislike up with violations.
IMO, 408.3 only applies to equipment used on polyphase systems.
That is not what is says.
It says....
....."The phase arrangement on 3-phase buses shall be "....
It does not say "panels supplied with polyphase system".
IMO If the panel ships with 3 phase buses that section applies
]All I ever said was to check with the manufacturer not just assume based on appearances.
I am not assuming anything based on experience I am saying we must follow the listing and labeling provided.
According to the Square D FAQs:
Question: Can we make a 120 volt only NQOD panelboard?
Answer: We can make a 120 volt only panelboard as a special. It can be main lug or main breaker type providing that a 1 pole breaker is available for use in the application. The bus bars in a 1 phase NQOD interior will be jumpered to create one continuous bus.
The key there is they can make one they did not say to make one in the field. I don't imagine they do much other than placing a jumper in and re-tagging the equipment for it's new use.
Truly I just don't understand your resistance to this, it seems very clearly a 110.3(B) issue.
If this is not, what is?