I want to give the latest in this.  The local inspector decided to side with the contractor on this one.  The contractor convinced the inspector his class 2 wiring is exempt from 300.17 because there is no heating effect.  I wrote this letter to the head inspector but have not gotten a reply yet:
_________________________________________________________________
I recently had a discussion with one of the cities inspectors ("Bob").  I explained to Mike that we are experiencing some problems with our low voltage contractors overfilling conduit (with class 2 wiring) on systems associated with air handling equipment.  Bob was not the inspector for this particular area so I was referred to Joe.  To make a long story fairly short it was determined that class 2 wiring is exempt from the conduit fill guidelines set forth by NFPA-70 (NEC).  It was my understanding that this was discussed among the group of inspectors and possibly yourself.
I would like a chance to plea my case with you and hope you will reconsider your ruling on this matter.  I know the code is not intended to make my life easy, this is not my concern.  As you know article 90 states ?This code contains provisions that are considered necessary for safety?.  It is my understanding that the overfilling of conduits containing class 2 wiring is not viewed as an ?unsafe? practice.  If this is accurate I would hope to change your opinion on this topic.
I?m not sure if article 725.11 fits in this case or not.  However, I do know some of the wiring associated with air handling equipment is intended for reducing fire and life hazards and beyond that preventing building damage.  To name a few there are systems which will shut down air handlers in case of fires to prevent fire from spreading, systems to turn on stairwell pressurization fans to keep smoke out of stairwells, and there are systems intended to prevent heating/cooling coils from rupturing and spilling their contents.  Any damage done to wires during installation could prevent these systems from working as designed.
Article  725.3 states ?Circuits and equipment shall comply with the articles or sections listed in 725.3 (A) through 725.3 (G).  Only those sections of Article 300 referenced in this article shall apply to Class 1, Class 2, and Class 3 circuits.?
725.3 (A) reads ?Number and Size of Conductors in Raceway.  Section 300.17.?
If you then read 300.17 you will see where it says ??not be more than will permit dissipation of the heat and ready installation or withdrawal of the conductors without damage to the conductors or to their insulation.?
The conduit which started this whole mess is 81% full (a generously small measurement)!  I am pretty sure we would agree this type of fill is likely to damage something during the installation and if not then most likely the first time something needs to be changed.  I think where we may disagree is on whether or not this prevents a life safety issue.  I hope you will consider what I have written here and discuss it with others.  In my opinion it is not only poor practice is also dangerous.
Thank you for your time,
*me*
The reason I post this is I would like to know what others think about this topic.  Let's hear it.