II. Branch-Circuit Ratings
210.19 Conductors ? Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an am-
pacity not less than the maximum load to be served. Where
a branch circuit supplies continuous loads or any combina-
tion of continuous and noncontinuous loads, the minimum
branch-circuit conductor size, before the application of any
adjustment or correction factors, shall have an allowable am-
pacity not less than the noncontinuous load plus 125 percent
of the continuous load.