Here is the problem:
Generator normally operates in parallel with the power grid. Grid is at 12.47 kV with a wye-wye transformer going down to 480V.
The customer owns the transformer.
The original design had the N & G bonded at the wye wye transformer, the 480V breaker, and at the 480V MCC.
I should note there is no Neutral load at the plant
**The problem is the high neutral current, which is about 7-800A** The attached sketch was how the unit was installed. Granted, the wye-wye xfmr may exasperate this problem, but I am thinking of the following:
-> Disconnect all of the N-G Bonds except at the xfmr
->Add in a low resistance ground
->Disconnect the neutral of the generator........
Any suggestions?
Any suggestions?