Kalyan
- Kansas City, Mo, USA
I have a situation at a PV installation where the point to point fault current had to be limited to 10000 A. Hence as per the fault current calculation for a 2/0 wire with a 14,318A fault current available at point 1(line tap), i had to make the conductor length at least 40ft to be able to achieve the less than 10000A fault current at point 2 (PV system disconnect). The wire size has to stay at 2/0 as per utility. With just 5 ft physical distance between Point 1 and Point 2, the only way to accommodate 40ft is to coil the excess conductors in a jbox (Which is almost next to impossible for a 2/0 wire size). Are there any restrictions as per NEC or any other safety/ good practices that would stop me from coiling the conductors? Please suggest any alternative methods for making this work.
See the attached rough sketch to help give you a better understanding.