D domnic Senior Member Occupation Electrical Contractor Apr 3, 2008 #1 Can i run romex through a cold air return in a single story one family home? code section please.
mdshunk Senior Member Location Right here. Apr 3, 2008 #2 Horizontally only. ...check that; perpendicular I should say.
ryan_618 Senior Member Location Salt Lake City, Utah Apr 3, 2008 #3 domnic said: Can i run romex through a cold air return in a single story one family home? code section please. Click to expand... 300.22(C).
domnic said: Can i run romex through a cold air return in a single story one family home? code section please. Click to expand... 300.22(C).
raider1 Senior Member Staff member Location Logan, Utah Apr 3, 2008 #4 To add to what the others have already stated, specifically look at the exception to 300.22(C). Chris
To add to what the others have already stated, specifically look at the exception to 300.22(C). Chris