COLD METER SEQUENCING

Status
Not open for further replies.

alanchk

Member
DISCONNECT IS BEFORE METER.
ABOVE DISC, IS USED TO DE ENERGIZE METER.
DO I NEED A SERVICE DISC. ALSO?
WHAT ABOUT GROUNDING??
:confused:
 
Re: COLD METER SEQUENCING

tURN oFF yOUR cAPS lOCK. Thanks
It depends on your POCO what they will allow. If they want the disconnect ahead of the meter locked, its "kindof" their disconnect.
I have been installing disconects ahead of the meter for 25 years. Some I consider a service disconnect, most are non-fused and locked by the POCO.
But watch the available fault current a non fused disconnect is typically 10,000 AIC rated
 