SKM sorts you into orange and red labels based on the PPE table you choose. It used to be impossible to find PPE rated for 40 Cal/cm², although that has changed. But the default table still breaks off at 40 Cal.So 40.01cal/cm2 is unsafe but 39.99 is perfectly safe?
These must be customer specific break points, because NFPA 70E does not contain any color coding.
I have never found utility side primary fuses to make much different on my customer's service equipment arc flash values.
Your right, with a standard impedance transformer the AF energy isn't affected much by a line side fuse, but it you use a transformer with %Z in the 1.5 - 2.5 range you'll see a difference.