Re: COLD WATER BOND
Or, are you talking about the point of connection for the other end of the bonding conductor for the metal water piping? 250.104(A)(1) requires that to be the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor, or one of the grounding electrodes. No mention there of a subpanel.
[ February 13, 2004, 03:30 PM: Message edited by: eprice ]