Indeed, and I stand by my reading. The key part of 250.68(C)(1) is "used as a conductor to interconnect electrodes". If you're not using the water pipe in that fashion, there is no 5 foot rule. You can connect your GEC or bonding jumper to the water pipe electrode anywhere that is electrically continuous with the underground section as per 250.52(A)(1).Read (C) and (C)(1) carefully.
Look as 250.68(C)(2), it is about using the structural frame of a building to interconnect electrodes. All of 250.68 is about interconnecting electrodes, not how to connect to a single electrode.
Cheers, Wayne