Hello,
I work for a company which designs and builds control panels per UL508A. We have difference of opinion here concerning what color to run a specific wire.
Motor control circuit is being supplied by 120vac control transformer with grounded secondary. NC contact of overload relay is located on grounded circuit conductor side of contactor coil. What color wire should be run between overload contact and coil.
Is this still considered a grounded circuit conductor after it passes through NC contact of overload and should be continued with white wire? or should it be considered part of the 120v circuit and run with red wire.
UL508A is not clear on this.
Normally we would locate overload contact on ungrounded side of coil,but in this case we are using customer drawings.
Thank you for any insight anyone can provide on which is correct or common practice.