There is no NEC required color scheme for general use circuits at any voltage. Except for white, gray, and green you can use any color you want.What is the proper color code for 277/480 and is it county, or state wide. where do I find it in the code book
I'm way too lazy to look it up right now but is't there an orange required for a high leg or something?
What is the proper color code for 277/480 and is it county, or state wide. where do I find it in the code book
That could be trouble. When I wire the microswitches for commercial-kitchen fire-suppression systems, I sometimes need six colors, and orange is one of them. I use black, red, blue, brown, orange, and yellow. White for grounded, of course, and an occasional purple. But, I mix the colors between switches so nobody thinks one micro is handling only 120v and the other only 277v.according to the pse&g hand book orange cant be used unless high leg is present.
That should not be an issue...the utility company rules do not extend beyond the service equipment...actually they stop at the service point with the exception of a meter that is installed on the load side of the service point.That could be trouble. When I wire the microswitches for commercial-kitchen fire-suppression systems, I sometimes need six colors, and orange is one of them. I use black, red, blue, brown, orange, and yellow. White for grounded, of course, and an occasional purple. But, I mix the colors between switches so nobody thinks one micro is handling only 120v and the other only 277v.
Ah, my bad. I missed the PSE&G reference.That should not be an issue...the utility company rules do not extend beyond the service equipment...
I beleive it used to be code brown,orange,yellow 277/480 and black, red , blue 120/240 in the 93 code?? but has since changed to any color for branch circuits except for the bastard leg.
In 1940 they swapped the blue and yellow.Branch circuits of any of the types recognized in this article may be installed as multi-wire circuts; provided one of the conductors of the circuit is an identified grounded conductor. Conductors of such multi-wire branch circuits of multi-phase systems shall conform to the following color code: three-wire circuits-- one black, one white, one red; four-wire circuits-- one black, one white, one red, one yellow; five-wire circuits-- one black, one white, one red, one yellow, one blue.
1975:210-5(c) was simply:All ungrounded conductors of the same color shall be connected to the same ungrounded feeder conductor and the conductors for systems of different voltages shall be of different colors.
It is recommended for a basic single wiring system that the following colors be used: 3-wire circuits-- 1 black, 1 white, 1 red; 4-wire circuits-- 1 black, 1 white, 1 red, and 1 blue.
Ungrounded conductors of different voltages shall be of different color or identified by other means.
That could be trouble. When I wire the microswitches for commercial-kitchen fire-suppression systems, I sometimes need six colors, and orange is one of them. I use black, red, blue, brown, orange, and yellow. White for grounded, of course, and an occasional purple. But, I mix the colors between switches so nobody thinks one micro is handling only 120v and the other only 277v.