I just tried to renew my license, with my luck, the state website crashed before I hit the "submit" button. :roll:

Anyway, there was a question that drew my interest:

The minimum size copper grounding electrode conductor required to a concrete-encased electrode is:

A.) 8 AWG
B.) 6 AWG
C.) 4 AWG
D.) 2 AWG

What say you - or better still, what answer do you think they're expecting to hear?
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Stickboy1375 said:
C - #4 Awg
My thoughts are, I wonder if the writer of the test would concur with Stickboy's answer.
baldguy.gif
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
That's a maximum, not a minimum. This is the sort of question that makes me start second-guessing what they intended to ask.

I hate stupid test questions being tricky for tricky's sake. :mad:
 

stickboy1375

Senior Member
Location
Litchfield, CT
I would have to say the answer is #8 cu, since you have to use table 250.66
Thats the smallest size copper wire they have listed, but obviously I got that wrong since I read 250.66 (B) first...:grin: :grin: :grin:
 

ryan_618

Senior Member
georgestolz said:
That's a maximum, not a minimum. This is the sort of question that makes me start second-guessing what they intended to ask.

I hate stupid test questions being tricky for tricky's sake. :mad:

I've been asked by the International Code Council to serve on their Electrical Exam Development comittee. I'll be sure to add questions like this, just for you George. :D

I'll tell you what I do on questions like this...I challenge them...all of them, before I even know my test score. I write down why the answer is 8 AWG, just in case the question is worded wrong, or in case the person who wrote the question made a mistake. I remember challenging a few of the questions when I did my electrical plans examiner test, but the challenges didn't get reviewed because I passed the first time :(
 

stickboy1375

Senior Member
Location
Litchfield, CT
JohnJ0906 said:
My teachers in apprentice school would mark "#8" as incorrect. You were supposed to write, "#8 in armor" (250.64(B)):roll:

Grounding conductors smaller than 6 AWG shall be in RMC, IMC, rigid nometallic conduit, EMT, or cable armor.

why would you say just "in armor"?
 

Jljohnson

Senior Member
Location
Colorado
I looked at that question a little bit differently George. 250.52(A)3 says that the CEE can be MADE from bare copper. Miminum of 20' long and # 4 Bare.
I answered "C".
 

FrancisDoody

Senior Member
Location
Durham, CT
I don't see any ambiquity in the question. NEC 250.52 A (3) is very clear that if you elect to use a bare copper conductor as your electrode it has to be no smaller than a #4. So I agree with Stickboy and everyone else who selected "C" as thier answer.
Thanks,
Fran
 

JohnJ0906

Senior Member
Location
Baltimore, MD
stickboy1375 said:
Grounding conductors smaller than 6 AWG shall be in RMC, IMC, rigid nometallic conduit, EMT, or cable armor.

why would you say just "in armor"?
Because that was the answer they required! IMO, it was a reminder to us that it had to be protected.
 