Is there a code for color coding of
120 volt outlets
208 v
480v
also emergency power
24 volt
Dave
120 volt outlets
208 v
480v
also emergency power
24 volt
Dave
480sparky said:Nothing required by the NEC, but there is an 'unofficial' color colde
Black/Red & White for 120/240
Black/Red/Blue & White for 120/208
Brown/Orange/Yellow & Greay for 277/480.
dcspector said:Dave, as mentioned above colors are Industry standards. Check with the local AHJ for their requirements. Here in DC (DCRA required) it is Black, Red, Blue, White 208/120 and Brown Orange, Yellow, Gray 480/277
jwelectric said:I ask you also what do you do with a three phase 240/120 system?
jwelectric said:I ask you also what do you do with a three phase 240/120 system?
David Bonin said:Is there a code for color coding of
120 volt outlets
208 v
480v
also emergency power
24 volt
Dave
480sparky said:Or, you could just use this stuff.
A 240/120 three phase system will have one leg that is 208 volts and 110.15 requires this leg to be identified by the color ORANGE480sparky said:You can use any colors you want for ungrounded except green, grey or white.
jwelectric said:A 240/120 three phase system will have one leg that is 208 volts and 110.15 requires this leg to be identified by the color ORANGE
jwelectric said:A 240/120 three phase system will have one leg that is 208 volts
jwelectric said:A 240/120 three phase system will have one leg that is 208 volts and 110.15 requires this leg to be identified by the color ORANGE
jerm said:Probably a stupid question... Aren't there 120/240 3o Wye systems? Or are all 120/240 3o systems Delta?