sparks1
Senior Member
- Location
- Massachusetts
Where does it say in code that wires should be taped for different voltage systems such as black ,red, blue for 120/208 and brown,orange, yellow for 277/480.
It doesn't.Originally posted by sparks1:
Where does it say in code that wires should be taped for different voltage systems such as black ,red, blue for 120/208 and brown,orange, yellow for 277/480.
Thank goodness for that! I would not like to see an inspection fail for no better reason than the wrong colors were used. More importantly, from a safety perspective, I would not want a person to say, "I turned off the 480 circuit, and that wire is the color of a 480 circuit, so I can safely disconnect that wire."Originally posted by sparks1:This could mean any color tape could be used!
The same wording appears in 215.12(C) for feeders. Note that the requirement is only to identify by system, not by phase and system, so all of the 120/208 ungrounded conductors could be black and all of the 277/480 conductors could be red.210.5(C) Ungrounded Conductors. Where the premises wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a
branch circuit, where accessible, shall be identified by system. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each
branch-circuit panelboard or similar distribution equipment.
Brian I do not understand there is no 'correct' color / rotation method.Originally posted by brian john:
The number of times we see incorrect rotation with the correct colors, or electricians wiring BYO, OYB, YOB and all swearing the code backs their method. ROTATION, ROTATION, ROTATION
Again I ask what is 'correct'?Originally posted by sparks1:
we correctly retape the violations on old work after the voltage has been established
Correct, that is what I was getting at.Originally posted by sparks1:
The means of identification shall be permitted to be by separate color coding.
But it doesn't say what color code we should use.
What violation are you correcting?we correctly retape the violations on old work after the voltage has been established
But there is no standard, there is only what you are used to.in my opinion, using this as a "Standard" enhances over all safety.
What about 408.3(E)?That said from the first connection to the utility there is no telling if what we landed on "A" and marked brown is actually phase A or will produce clockwise rotation.
What about it?Originally posted by don_resqcapt19:
Bob,
What about 408.3(E)?That said from the first connection to the utility there is no telling if what we landed on "A" and marked brown is actually phase A or will produce clockwise rotation.
Don
Originally posted by iwire:
Correct, that is what I was getting at.Originally posted by sparks1:
[qb] The means of identification shall be permitted to be by separate color coding.
But it doesn't say what color code we should use.
You had said;
What violation are you correcting?we correctly retape the violations on old work after the voltage has been established
If adding a new circuit or part of a circuit to an existing scheme that has colors other than (BRB)or(BOY), It is standard practice here in MA to identify the wires (BRB)OR(BOY)all the way back to the breaker.