Columns B and C in T220.55 (NEC2023)

Status
Not open for further replies.

Abraham V

Member
Location
MN, USA
Occupation
Student
When applying T220.55, we can get two different answers for the same scenario.
Ex. 1: 1 x 8kW range is @ 6.4 kW in Column B and 8 kW in Column C.
Ex. 2: 40 x 8kW ranges is @ 70.4 kW in Column B and 55 kW in Column C.

In these situations, should I be trying both methods and using the one that results in the smallest demand value? Or is there some secret about which is better after a certain number of units, eliminating the need to do that?
 
Don't have the table in front of me, but do the footnotes even allow the use of column B with ranges? We are instructed to use column C unless permitted otherwise in the footnotes.

Cheers, Wayne
 
My thinking is that the smaller size should be used however there is no telling what the tester will want. Hopefully you wont get a question like that
 
The scenarios I wrote are from Example D4(b): Ex 1. from Application of Demand Factor and Ex 2. from Feeder Neutral Load of Main Feeder (Less House Load) (For 40 Dwelling Units). I don't see any rule they followed other than using what provided the smaller value. I suppose there is no other reason to use two different methods in the same question.

Thanks, gents.
 