Combination AF GFCI protection

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
I don’t believe so, or at least not readily available now.

What is it for? AFCI is only required on 120 volt circuits currently, (2020 NEC), so the only place you would conceivably need a 2P AFCI would be for a MWBC, so you could use 2, 20A GFCI/AFCI 1P and use a handle tie.
 

Jim L

Member
Location
Port Charlotte fl
Occupation
Electrician
I don’t believe so, or at least not readily available now.

What is it for? AFCI is only required on 120 volt circuits currently, (2020 NEC), so the only place you would conceivably need a 2P AFCI would be for a MWBC, so you could use 2, 20A GFCI/AFCI 1P and use a handle tie.
I’m hoping that 2 kitchen circuits, sharing a 12/3 could be protected, and avoid pulling in an additional 12/2.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I don’t believe so, or at least not readily available now.

What is it for? AFCI is only required on 120 volt circuits currently, (2020 NEC), so the only place you would conceivably need a 2P AFCI would be for a MWBC, so you could use 2, 20A GFCI/AFCI 1P and use a handle tie.
You can't use two single pole GFCIs to supply a multiwire circuit.
 