A Alwayslearningelec Senior Member Location NJ Occupation Estimator Dec 8, 2023 #1 Per the attached and the highlighted HWH feed would you run a separate pipe for the 1" with #8's or run a larger pipe to the area combining some other circuits.
Per the attached and the highlighted HWH feed would you run a separate pipe for the 1" with #8's or run a larger pipe to the area combining some other circuits.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Dec 8, 2023 #2 Depends. You'd have to compare costs and hours of doing it each way. Conductor fill and derating apply. If the loads are concentrated enough, consider a nearby feeder and sub-panel.
Depends. You'd have to compare costs and hours of doing it each way. Conductor fill and derating apply. If the loads are concentrated enough, consider a nearby feeder and sub-panel.